Concur.  It's not the EC/SC thing, it's the RTI thing.  QR shouldn't be
mixed with SR but listed coverage area not an issue.   If you think
about it, mixing those different discharge characteristics is similar to
mixing sidewalls and pendents in the same compartment and we do that all
the time, especially in residential occupancies, no?

SL 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
John Denhardt
Sent: Wednesday, May 28, 2014 9:36 AM
To: <[email protected]>
Subject: Re: Mixing EC-QR and SC-QR sprinklers in the same area

Agree 100%

Thanks,
John August Denhardt P.E.

> On May 28, 2014, at 12:32 PM, "[email protected]"
<[email protected]> wrote:
> 
> Yes, they can be mixed. We do it all the time. SC in entry and EC in
sleeping room.
> Ron F
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Pete Schwab
> Sent: Wednesday, May 28, 2014 8:49 AM
> To: [email protected]
> Subject: RE: Mixing EC-QR and SC-QR sprinklers in the same area
> 
> Did you mean to say EC Standard response with QR elements mixed with
standard coverage QR?
> 
> 
> Peter Schwab
> VP of Purchasing & Engineering Technologies
> 
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
> 
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
> 
> www.waynefire.com
> 
> 
> 
> We're hiring great people at all of our locations!  Please check out
our website for the details! 
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Sean Lockyer
> Sent: Wednesday, May 28, 2014 11:19 AM
> To: [email protected]
> Subject: Mixing EC-QR and SC-QR sprinklers in the same area
> 
> Can Extended Coverage Quick Response Sprinklers and Standard Coverage
Quick Response Sprinklers be mixed in the same compartment ? Even though
QR and SR cannot be mixed within the same compartment (I.E.-Room) there
is no rule precluding the mixing of EC-QR and SC-QR heads as far as I
know.
> 
> Does anyone here have any experience in this area ?
> 
>               Sean Lockyer
>               Project Designer                               4617
Parkbreeze Court
>               Cell    386-279-1197
Orlando, Florida 32808
>               [email protected]              Phone:
407-816-9101
>               www.AITLifeSafety.com                       Fax:
407-816-9104
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to