Concur. It's not the EC/SC thing, it's the RTI thing. QR shouldn't be mixed with SR but listed coverage area not an issue. If you think about it, mixing those different discharge characteristics is similar to mixing sidewalls and pendents in the same compartment and we do that all the time, especially in residential occupancies, no?
SL -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of John Denhardt Sent: Wednesday, May 28, 2014 9:36 AM To: <[email protected]> Subject: Re: Mixing EC-QR and SC-QR sprinklers in the same area Agree 100% Thanks, John August Denhardt P.E. > On May 28, 2014, at 12:32 PM, "[email protected]" <[email protected]> wrote: > > Yes, they can be mixed. We do it all the time. SC in entry and EC in sleeping room. > Ron F > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] On Behalf Of Pete Schwab > Sent: Wednesday, May 28, 2014 8:49 AM > To: [email protected] > Subject: RE: Mixing EC-QR and SC-QR sprinklers in the same area > > Did you mean to say EC Standard response with QR elements mixed with standard coverage QR? > > > Peter Schwab > VP of Purchasing & Engineering Technologies > > Wayne Automatic Fire Sprinklers Inc. > 222 Capitol Court > Ocoee, Fl 34761 > > Mobile: (407) 468-8248 > Direct: (407) 877-5570 > Fax: (407) 656-8026 > > www.waynefire.com > > > > We're hiring great people at all of our locations! Please check out our website for the details! > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] On Behalf Of Sean Lockyer > Sent: Wednesday, May 28, 2014 11:19 AM > To: [email protected] > Subject: Mixing EC-QR and SC-QR sprinklers in the same area > > Can Extended Coverage Quick Response Sprinklers and Standard Coverage Quick Response Sprinklers be mixed in the same compartment ? Even though QR and SR cannot be mixed within the same compartment (I.E.-Room) there is no rule precluding the mixing of EC-QR and SC-QR heads as far as I know. > > Does anyone here have any experience in this area ? > > Sean Lockyer > Project Designer 4617 Parkbreeze Court > Cell 386-279-1197 Orlando, Florida 32808 > [email protected] Phone: 407-816-9101 > www.AITLifeSafety.com Fax: 407-816-9104 > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org