It depends,  If it is a multi-story builing you need one at every alternate
level, offset, bottom, top and no more than 25'-0" apart.   If it's not a
multistory, just 1 hanger ring at the top of the riser within 24"

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Friday, June 13, 2014 9:52 AM
To: [email protected]
Subject: Support of tall risers

Where "seismic" is not required, and the riser is, say, 6" by 35 feet tall,
is there a requirement or rule of thumb for the vertical spacing for the
support of it?

A co-worker and I thank you in advance.

 