Thanks Jerry. We got some off-Forum feedback also and are convinced the best practice would be at least one support per piece, so are thinking max spacing should be 21'-0". The feedback was from a contractor who does grain elevators with VERY tall risers and they use half-lengths with a support on each piece!
Brad -----Original Message----- From: Jeremy Frazier [mailto:[email protected]] Sent: Friday, June 13, 2014 2:01 PM To: [email protected] Subject: RE: Support of tall risers It depends, If it is a multi-story builing you need one at every alternate level, offset, bottom, top and no more than 25'-0" apart. If it's not a multistory, just 1 hanger ring at the top of the riser within 24" -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brad Casterline Sent: Friday, June 13, 2014 9:52 AM To: [email protected] Subject: Support of tall risers Where "seismic" is not required, and the riser is, say, 6" by 35 feet tall, is there a requirement or rule of thumb for the vertical spacing for the support of it? A co-worker and I thank you in advance. Brad Casterline, NICET IV Fire Protection Division FSC, Inc. P: 913-722-3473 [email protected] www.fsc-inc.com Engineering Solutions for the Built Environment _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org