Easy to do with a dead end system but not so easy with a gridded system

*Thanks*

*Rahe Loftin, PE  *
*Regional Fire Protection Engineer*
*General Services Administration*
*Region 7 - TX, OK, NM, AR, LA*
*Facilities Management & Support 7PMC*
*c - 817-371-3102*
*o - 817-978-7299*


On Thu, Jun 26, 2014 at 11:58 AM, Brad Casterline <[email protected]>
wrote:

> Makes sense Todd.
>
> I believe a flow test measures the friction loss from the source to the
> gauged hydrant, with a negligible amount of velocity head loss. Say we get
> 75,72,500. If we know 8" X 1500 feet total, using Q^1.85 and rearranging
> H-W, we can get the C-Factor=140. If we got 75,68,500 with the same 8 by
> 1500, we would get C=85. Also, using Q^2 and C=140, we would get the same 7
> pound drop. I guess what I am saying is, the flow test is a measure of the
> several factors, as a whole, that are usually unknown without doing a lot
> of
> digging, literally ;)
>
> Brad
>
>
> -----Original Message-----
> From: Todd - Work [mailto:[email protected]]
> Sent: Thursday, June 26, 2014 10:18 AM
> To: [email protected]
> Subject: Re: Underground Piping
>
> Remember, all of our formulas are approximations. They can be more accurate
> in some situations and less in others. The velocity restrictions of years
> back were originally to compensate for the inaccuracies in the formula when
> velocity exceeded a certain amount.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to