Bob
What is the hazard and ceiling height? Can you take an area reduction and
calc even fewer heads?
Bill Cunningham
Plumbco Inc.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Friday, June 27, 2014 10:12 AM
To: [email protected]
Subject: Cooler Calc

I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and
submitted.  The AHJ is telling me that I need to calc additional sprinklers
at the ceiling to have a 1500 sf design area.  I don't think I need to do
this, I was looking at this as a separate fire area, and I don't see it
being much different than not adding heads below ducts or other large
obstructions.  Do I need to calc additional sprinklers at the ceiling for
this application?

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com