Bob, It looks like you want to use the room design method. You only need to calc all sprk's in room calc as long as the walls enclosing the room have a fire resistance rating equal to or greater than the corresponding water supply duration requirement for the particular hazard.
If you don't use the room design method, then 1500 sq.ft. Unless you apply a reduction. Sean W. Conlin Demand Sprinkler Design Inc. On 2014-06-27, at 1:32 PM, "Bill Cunningham" <[email protected]> wrote: > Bob > What is the hazard and ceiling height? Can you take an area reduction and > calc even fewer heads? > Bill Cunningham > Plumbco Inc. > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Bob > Sent: Friday, June 27, 2014 10:12 AM > To: [email protected] > Subject: Cooler Calc > > I have a 1,392 sf cooler. I calc'ed the entire area of the cooler and > submitted. The AHJ is telling me that I need to calc additional sprinklers > at the ceiling to have a 1500 sf design area. I don't think I need to do > this, I was looking at this as a separate fire area, and I don't see it > being much different than not adding heads below ducts or other large > obstructions. Do I need to calc additional sprinklers at the ceiling for > this application? > > Thank You, > > Bob Knight, CET III > 208-318-3057 > www.Firebyknight.com > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org