If the warehouse is unheated, that is, if there is a chance of freezing, it is 
my opinion that it would be doubtfulto find a single interlock preaction 
system; therefore, it would likely be a double interlock.  You could look at 
the design area on the hydraulic placard ( if there is one) as one way of 
making the determination.  Take a look at the trim, and if you do not see a 
pneumatic actuator in addition to the solenoid, it is likely that it is an 
electric-electric type double interlock system.  This can be verified by 
looking at the releasing panel input zones and determining if the low air 
pressure switch is wired into an alarm zone rather than a low air supervisory 
zone. Of course, you can verify the manufacturer and compare to the data sheets 
as well.

Regards,

Salvatore J. Izzo III, P.E.  SFPE
Manager - QA/QC Operations
Insurance Services Office
Verisk Commercial Real Estate
545 Washington Blvd.
Jersey City, NJ 07310 - 1686
t 201.469.2486
f 201.748.1942
c 732.533.7927
[email protected]
www.verisk.com/insurance

Verisk Insurance Solutions ● ISO | AIR Worldwide | Xactware
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, June 30, 2014 9:13 AM
To: [email protected]
Subject: RE: Identification of preaction system types

Ok, So what would be the tell-tale difference?

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, June 30, 2014 9:12 AM
To: '[email protected]'
Subject: RE: Identification of preaction system types

Nope. You have to look at the trim on the preaction valve.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Monday, June 30, 2014 9:09 AM
To: [email protected]
Subject: Identification of preaction system types

Can you identify the type of preaction system installed just by looking at the 
system riser?

I have a warehouse, unheated, Preaction system of unknown type.  There are heat 
detectors at the roof deck and there is a small air compressor.

That's all I've got to go on.  I can make assumptions all day long, but no 
assumption is better than an incorrect assumption at this point.

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________

This email is intended solely for the recipient. It may contain privileged, 
proprietary or confidential information or material. If you are not the 
intended recipient, please delete this email and any attachments and notify the 
sender of the error.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to