-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, July 28, 2014 2:38 PM
To: [email protected]
Subject: RE: UG Restraint

Is it listed restraint?   No.    Seems to be the answer to your
question, sliding pipe notwithstanding.

And what, exactly is sliding pipe?   I'm aware of mechanical joints, and
fused joints and flanged joints for underground piping.   But not
sliding pipe, so having my doubts about using a penetration seal for
something it's not listed to do.   Mechanical restraints have set screws
that hold the glands to the pipe being restrained; this one's a non-starter
for me.

SL

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Bob
Sent: Monday, July 28, 2014 1:28 PM
To: [email protected]
Subject: RE: UG Restraint

I don't see where this is explicitly stated, but there is an option that
will allow for "sliding pipe".  This leads me to believe that the assembly
restrains against movement.

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, July 28, 2014 2:26 PM
To: [email protected]; AFSA Sprinkler Forum (AFSA
SprinklerFORUM)
Subject: RE: UG Restraint

Is the assembly a listed restraint?   

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Bob
Sent: Monday, July 28, 2014 1:24 PM
To: AFSA Sprinkler Forum (AFSA SprinklerFORUM)
Subject: UG Restraint

When using a product such as linkseal or metraseal is it necessary to
install any form of restraint?  I haven't found anything on either products
data sheet that would point to this.  The situation I have is leaving one
lower level  wall traveling a short distance underground and then
penetrating another wall.  It looks like the assembly restrains as well as
seals, but I'm not certain about this.

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to