There's nothing in the 20 that says you can't take suction from a
different water supply for the jockey pump than the one that serves the
fire pump.  I'd say that the domestic supply should be reviewed by the
AHJ to assure that it meets the sniff test for reliability, though
that's not defined.   Any way you look at it, the J-pump is required to
be "approved".

Steve Leyton
Protection Design & Consulting
Anticipating Simon Shannon's Out of Office Reply

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Todd - Work
Sent: Wednesday, July 30, 2014 9:25 AM
To: [email protected]
Subject: jockey pump suction

A client in a rural area has a diesel VT fire pump taking suction from
an underground 30000 gallon cistern. Their domestic supply is fed from a
separate well. The jockey pump takes suction from the domestic water
supply. Is there a problem with this? There is a backflow preventer on
the jockey pump suction line. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)