Sounds like wood joist construction, in which case your area of coverage
will be significantly lower than the 168/225 you noted.   Could it be
panel construction - bays no greater than 300 sf?   Does a nominal 3 x 9
meet the intent and definition of "member capable of trapping heat?"
(Probably not ...)

SL

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Monday, August 04, 2014 11:02 AM
To: [email protected]
Subject: Obstructed or un=obstructed construction

NFPA13 (07ed)

3in wide / 9in deep wood beams 7ft on center.  Obstructed or
un-obstructed construction?  Just want to check because 168sf vs 225sf
spacing makes a big difference on this project.

Thanks,

Dewayne

 