No other members.  This is an old wood building with 6ft deep main wood
girders and the 3x9 holding up the wood deck.  They are converting if
from a OH II warehouse to an office. 

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Steve Leyton
Sent: Monday, August 04, 2014 1:46 PM
To: [email protected]
Subject: RE: Obstructed or un=obstructed construction

If that's the only member, yes.   But if there are 2x4 or other small
sub-purlins within the bays formed by these 3x9's, then you're down to
130 sf.

SL

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Monday, August 04, 2014 11:43 AM
To: [email protected]
Subject: RE: Obstructed or un=obstructed construction

I was figuring on 168sf but the way the definition is written threw me
off.  
Thanks

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Steve Leyton
Sent: Monday, August 04, 2014 1:28 PM
To: [email protected]
Subject: RE: Obstructed or un=obstructed construction

Sounds like wood joist construction, in which case your area of coverage
will be significantly lower than the 168/225 you noted.   Could it be
panel construction - bays no greater than 300 sf?   Does a nominal 3 x 9
meet the intent and definition of "member capable of trapping heat?"
(Probably not ...)

SL

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Monday, August 04, 2014 11:02 AM
To: [email protected]
Subject: Obstructed or un=obstructed construction

NFPA13 (07ed)

3in wide / 9in deep wood beams 7ft on center.  Obstructed or
un-obstructed construction?  Just want to check because 168sf vs 225sf
spacing makes a big difference on this project.

Thanks,

Dewayne

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to