Actually sprinklers (and most UL-listed equipment) are required to be pressure 
tested at 4x rated, so that would be 700 PSI for conventional sprinklers and 
1000 PSI for HP.

SL

 




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, August 06, 2014 9:08 AM
To: [email protected]
Subject: RE: Excessive system pressure and opening of sprinklers

Check the UL listing requirements, I believe the sprinkler heads are pressure 
tested at 500 PSI.
Mark at Aero

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, August 06, 2014 9:05 AM
To: [email protected]
Subject: Excessive system pressure and opening of sprinklers

Got a client that has had more than one incident of "accidental" sprinkler 
discharge they claim is due to municipal pressure surges.   Static pressure on 
this industrial system is 150 psi, and a surge tank was installed a couple of 
years back to mitigate alleged pressure spikes.  

Anyone heard of sprinklers opening due to a pressure spike?

It was only one head out of multiple hundreds in the building.   

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to