If it were due to a pressure spike than only one head opening might not be
unusual as the over pressure would be immediately relieved, but an unlikely
event nevertheless. Particularly multiple times unless a batch of bad
sprinklers. Think of pieces of pipe cut from a single pipe with a bad seam.
Then again when the forklift guy hits the sprinkler it usually is an
accident.


On Wed, Aug 6, 2014 at 9:28 AM, Steve Leyton <[email protected]>
wrote:

> Actually sprinklers (and most UL-listed equipment) are required to be
> pressure tested at 4x rated, so that would be 700 PSI for conventional
> sprinklers and 1000 PSI for HP.
>
> SL
>
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, August 06, 2014 9:08 AM
> To: [email protected]
> Subject: RE: Excessive system pressure and opening of sprinklers
>
> Check the UL listing requirements, I believe the sprinkler heads are
> pressure tested at 500 PSI.
> Mark at Aero
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, August 06, 2014 9:05 AM
> To: [email protected]
> Subject: Excessive system pressure and opening of sprinklers
>
> Got a client that has had more than one incident of "accidental" sprinkler
> discharge they claim is due to municipal pressure surges.   Static pressure
> on this industrial system is 150 psi, and a surge tank was installed a
> couple of years back to mitigate alleged pressure spikes.
>
> Anyone heard of sprinklers opening due to a pressure spike?
>
> It was only one head out of multiple hundreds in the building.
>
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to