If it were due to a pressure spike than only one head opening might not be unusual as the over pressure would be immediately relieved, but an unlikely event nevertheless. Particularly multiple times unless a batch of bad sprinklers. Think of pieces of pipe cut from a single pipe with a bad seam. Then again when the forklift guy hits the sprinkler it usually is an accident.
On Wed, Aug 6, 2014 at 9:28 AM, Steve Leyton <[email protected]> wrote: > Actually sprinklers (and most UL-listed equipment) are required to be > pressure tested at 4x rated, so that would be 700 PSI for conventional > sprinklers and 1000 PSI for HP. > > SL > > > > > > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] On Behalf Of > [email protected] > Sent: Wednesday, August 06, 2014 9:08 AM > To: [email protected] > Subject: RE: Excessive system pressure and opening of sprinklers > > Check the UL listing requirements, I believe the sprinkler heads are > pressure tested at 500 PSI. > Mark at Aero > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] On Behalf Of > [email protected] > Sent: Wednesday, August 06, 2014 9:05 AM > To: [email protected] > Subject: Excessive system pressure and opening of sprinklers > > Got a client that has had more than one incident of "accidental" sprinkler > discharge they claim is due to municipal pressure surges. Static pressure > on this industrial system is 150 psi, and a surge tank was installed a > couple of years back to mitigate alleged pressure spikes. > > Anyone heard of sprinklers opening due to a pressure spike? > > It was only one head out of multiple hundreds in the building. > > Craig L. Prahl > Fire Protection Group Lead > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29303 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org