Lamar, NFPA 13 (1987 edition) Chapter 5-2.3.1
Volume Limitations. Not more than 750-gal (2539 L) system capacity shall be controlled by one dry-pipe valve. Gridded dry-pipe systems shall not be installed. Jack W. Carlson, SET Triple "A" Fire Protection -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Lamar Vaughn Sent: Tuesday, August 19, 2014 9:22 AM To: Sprinkler Forum Subject: Gridded Dry Pipe System I have encountered a gridded dry system in a parking structure. Can someone tell me in what years gridded dry systems were allowed by NFPA 13? I don't recall it ever being allowed. Thanks, Lamar Vaughn, SET _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org