Thanks Richard and Jack for the help!
On Tue, Aug 19, 2014 at 9:40 AM, Jack Carlson <[email protected]> wrote: > Lamar, > > NFPA 13 (1987 edition) Chapter 5-2.3.1 > > Volume Limitations. Not more than 750-gal (2539 L) system capacity shall > be controlled by one dry-pipe valve. Gridded dry-pipe systems shall not be > installed. > > > Jack W. Carlson, SET > Triple "A" Fire Protection > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] On Behalf Of Lamar Vaughn > Sent: Tuesday, August 19, 2014 9:22 AM > To: Sprinkler Forum > Subject: Gridded Dry Pipe System > > I have encountered a gridded dry system in a parking structure. Can > someone tell me in what years gridded dry systems were allowed by NFPA 13? > I don't recall it ever being allowed. > > Thanks, > > Lamar Vaughn, SET > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org