Thanks Richard and Jack for the help!

On Tue, Aug 19, 2014 at 9:40 AM, Jack Carlson <[email protected]> wrote:

> Lamar,
>
> NFPA 13 (1987 edition) Chapter 5-2.3.1
>
> Volume Limitations.  Not more than 750-gal (2539 L) system capacity shall
> be controlled by one dry-pipe valve.  Gridded dry-pipe systems shall not be
> installed.
>
>
> Jack W. Carlson, SET
> Triple "A" Fire Protection
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Lamar Vaughn
> Sent: Tuesday, August 19, 2014 9:22 AM
> To: Sprinkler Forum
> Subject: Gridded Dry Pipe System
>
> I have encountered a gridded dry system in a parking structure. Can
> someone tell me in what years gridded dry systems were allowed by NFPA 13?
> I don't recall it ever being allowed.
>
> Thanks,
>
> Lamar Vaughn, SET