In Seattle the rule was, and may still be but I haven't worked in industry
for some time, that a six head or less T.I. didn't require an inspection,
but that was local to Seattle.


On Thu, Aug 21, 2014 at 5:11 AM, Greg McGahan <[email protected]> wrote:

> * NFPA #25.2.1.4* says that modifications affecting less than 20 sprinklers
> does not require hydrostatic testing...we regularly have inspections for 1
> and 2 head mods...
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>
>
> On Wed, Aug 20, 2014 at 2:10 PM, Charles Thurston <[email protected]>
> wrote:
>
> > Hello Sprinklerforum,
> >
> >   I have been told verbally by an AHJ in the area that systems under 20
> > heads do not have to be inspected. He said it was in the code, But has
> not
> > been able to pinpoint where.  I am unable to find that code reference,
> > Anybody know where it would be?
> >
> > --
> > Best regards,
> >  Charles                          mailto:[email protected]
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to