Good morning Ladies/Gentlemen:
 
I do not know where < 20 sprinklers might be found in 25  (or any other 
standard) and/or why there would be such a stipulation in the  first 
place...That said: IF an overwhelming number of  failures attributed to 
sprinkler 
systems (all sizes) are due  to closed valves and/or inadequate water supplies, 
it seems 'logical' that, if a  sprinkler system has a water supply and/or 
control valve, those devices would  need to be check/tested/inspected, 
regardless of the number of sprinklers in the  system?? The number '20' has 
been 
bandied around for years as to adding that  number of heads to an existing 
system, plans submittals, whether a hydro was  required, FDC requirement, etc.
 
In my professional (albeit humble) opinion, ALL fire sprinkler  systems 
need to be inspected/tested per NFPA-25 guidelines. I rather suspect our  
friends in the insurance industry would concur. In New Mexico, it is quarterly 
-  
it is statewide (commercial systems).
 
Best to All-
 
Jerry
[email protected]_ (mailto:[email protected]) 
 
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico (a U.S. State)
(800) 503.1961 nationwide
 
*Founded 1991
 
 
 
In a message dated 8/21/2014 9:29:26 A.M. Mountain Daylight Time,  
[email protected] writes:

In  Seattle the rule was, and may still be but I haven't worked in industry
for  some time, that a six head or less T.I. didn't require an inspection,
but  that was local to Seattle.


On Thu, Aug 21, 2014 at 5:11 AM, Greg  McGahan <[email protected]> 
wrote:

> * NFPA #25.2.1.4*  says that modifications affecting less than 20 
sprinklers
> does not  require hydrostatic testing...we regularly have inspections for 
1
> and  2 head mods...
>
>
> Greg McGahan
> Living Water Fire  Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie  Road
> Cantonment, FL 32533
> 850-937-1850
> fax  850-937-1852
>
>
> On Wed, Aug 20, 2014 at 2:10 PM, Charles  Thurston <[email protected]>
> wrote:
>
> > Hello  Sprinklerforum,
> >
> >   I have been told  verbally by an AHJ in the area that systems under 20
> > heads do not  have to be inspected. He said it was in the code, But has
> not
>  > been able to pinpoint where.  I am unable to find that code  reference,
> > Anybody know where it would be?
> >
>  > --
> > Best regards,
> >  Charles      mailto:[email protected]
> >
> >  _______________________________________________
> > Sprinklerforum  mailing list
> > [email protected]
>  >
> >
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  >
> _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--  
Ron Greenman
Instructor
Fire Protection Engineering  Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA  98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700  (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC

They are happy men whose natures sort with their  vocations. -Francis Bacon,
essayist, philosopher, and statesman  (1561-1626)

A problem well stated is a problem half solved. -Charles F.  Kettering,
inventor and engineer  (1876-1958)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to