A question has come up that in Table 17.2.3.1 the column that states Maximum 
Ceiling/Roof Height applies to the maximum Ceiling/Roof height of the building, 
not the storage area. As an example, if a warehouse has cartoned expanded 
plastics storage to 25' high in a portion of the warehouse that has a 
roof/ceiling height of under 32', but the ridge height of the building is 
33'-0, they are suggesting that the cartoned expanded plastic cannot be stored 
in the building  because the ridge height (not the area of storage) is above 
32'.  There reasoning is that the table applies to the entire building, not the 
area of storage.  Therefore if the highest point of the building exceeds the 
list table height, even though the storage area roof height is under the table 
height, the table cannot apply.  Is this a correct assumption or is the maximum 
height meant to apply to the area of storage?  



Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org