Greg,
I would look at the definition of ceiling height in 3.3.3:
3.3.3 Ceiling Height. The distance between the floor and the
underside of the ceiling above (or roof deck) within the area.
It would seem to me that this definition backs up the perspective that
Ron has added.
Has nothing to do with the roof height, only the height of the ceiling
in the area of storage.
If a storage area in a high rise had an 28' ceiling, and yet the
building was 22 floors high, you
certainly would not design based on a 22 story "ceiling height."
Just one perspective.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, CA 92025-5053
*****Phone 760.745.6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 8/21/2014 3:46 PM, [email protected] wrote:
I would say the maximum height is meant to apply the area of storage and not the maximum
height of the entire building. "A.17.2.3 Storage in single-story or multistory
buildings can be permitted, provided the maximum ceiling/roof height as specified in chapter
12 is satisfied for each storage area." If there were a high bay above 48' with in
racks and the remainder of the building was at <40' would you use area density with in
racks in the 40' area because there are no ESFR's listed for greater than 48'?
Ron F
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Gregg Fontes
Sent: Thursday, August 21, 2014 2:06 PM
To: [email protected]
Subject: ESFR Table 17.2.3.1 NFPA 13 2013
A question has come up that in Table 17.2.3.1 the column that states Maximum
Ceiling/Roof Height applies to the maximum Ceiling/Roof height of the building,
not the storage area. As an example, if a warehouse has cartoned expanded
plastics storage to 25' high in a portion of the warehouse that has a
roof/ceiling height of under 32', but the ridge height of the building is
33'-0, they are suggesting that the cartoned expanded plastic cannot be stored
in the building because the ridge height (not the area of storage) is above
32'. There reasoning is that the table applies to the entire building, not the
area of storage. Therefore if the highest point of the building exceeds the
list table height, even though the storage area roof height is under the table
height, the table cannot apply. Is this a correct assumption or is the maximum
height meant to apply to the area of storage?
Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org