Thanks Damien, especially for your excellent summary of some of the differences 
between NFPA and the European Code.
For the EC schedule with max 4 head line, using 32 ft/sec as the cut-off and 
130 ft2 spacing I got an average density of 0.192 GPM/ft2. For the NFPA 
schedule, using 20 ft/sec as the cut-off and 130 ft2 spacing I got an average 
density of 0.200 GPM/ft2.
So the next time I see a spec that limits the velocity I'll know that is from 
the old days- when the pipe size was the same whether the water supply was very 
poor or very good ;), and I will question everything else the specifier has to 
say!

Brad Casterline
AFSA Designer Member
 