When I joined Wormald in New Zealand 50 years ago they used this type of
table in the promotion of Fire Sprinkler systems.
The figures came from the records that Wormald kept on all sprinkler fires
in Australia and New Zealand. I also think that Mather and Platt did a
similar record in the UK.

In the book "Fire - Automatic Sprinklers in Australia and New Zealand 1886 -
1968" by Harry Marryatt there is very good analysis of that time period. It
was updated his 1986 edition which I think was called "A Century of Fire
Sprinklers"( I don't have a copy of the later book).
The figures in 1968 were;
66.6%   1 head
15.6%   2 heads
5.9%    3 heads
3.2%  4 heads
1.6%    5 heads
So 93% of sprinklered fires were 5 heads or less.
There were 5720 recorded fires in this study.
Satisfactory operation was 99.76% with 0.24% unsatisfactory incidents (14)

Wormald still keep a record of sprinkler saves on our systems, but the NZ
and Australian Fire Protection Associations and the NZ Fire Service try to
keep a full list, but it lacks the Technical Detail that was recorded for
over 100 years in the Wormald record.

Trust this is of interest.
Russell Gregory
Christchurch, New Zealand

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Frans Stoop
Sent: Thursday, 18 September 2014 4:53 a.m.
To: [email protected]
Subject: Sprinkler statistics

Gentlemen,

Once I saw a sprinkler statistic table saying something like this (I don't
remember the exact percentages):

Regarding fires that are succesfully controlled by sprinklers
50 % of the fires by 1 sprinkler
66 % of the fires by 1 or 2 sprinklers
75 % of the fires by upto 3 sprinklers
80 % of the fires by upto 4 sprinklers
83 % of the fires by upto 5 sprinklers
etcetera...

Does anyone recognize this table?
If so, any idea where I can find it?

I already found some statistics on the NFPA, AFSA, FM, SFPE and CIBV
websites, but couldn't find this simple table.

Met vriendelijke groet / Best regards,

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to