I thought I remembered it being 200 sq ft from years ago, but not really sure. It could have come from 800 sq ft max / 4 heads and you get 200 sq ft per sprinkler since you just do room size/#heads instead of distance from walls or between sprinklers for small room. Who knows...but it looks like 225 is the current number.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

On 9/26/2014 9:56 AM, Cliff Whitfield wrote:
Travis,

I just looked it up.  225 for hyd calc systems.  The 200 mentioned in Figure
A.8.6.3.2.4 (a) is for pipe schedule.  The 225 is shown directly below the
note for 200 sf.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
[email protected]
www.fire-design.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Friday, September 26, 2014 10:50 AM
To: [email protected]
Subject: Re: Small Room Rule

Actually, it is 200 sq ft per head, I believe when dealing with small
room exceptions.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

On 9/26/2014 9:43 AM, Cliff Whitfield wrote:
Yes.  You can be 16'6 per NFPA 13 when you utilize this rule.  You just
have
to be sure you don't exceed the 225 spacing per head.

I'm sending you a snapshot (directly to your email since we can't place an
attachment on the forum) that should answer your question.

Regards,

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
[email protected]
www.fire-design.com


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Friday, September 26, 2014 10:37 AM
To: [email protected]
Subject: RE: Small Room Rule

I hope this diagram go through. But something like this.

   _4_
|      |__14__
|                       |
16                  12
|____18___|

Every time there is more than a single heads in the figures it is 9' off a
wall then 6' off the opposite.  The question is can you space a sprinkler
16'6" in one direction and reduce the spacing in the other direction in
conjunction with multiple sprinkler when using small room?

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Cliff Whitfield
Sent: Friday, September 26, 2014 9:07 AM
To: [email protected]
Subject: RE: Small Room Rule

Jerry,

It's difficult to answer your question without seeing a true diagram of
your
room.  But in general, as long as you have a light hazard room that is
less
than 800 sf total, you can be up to 9' off of one wall and can have
multiple
heads in the room.  You can't be 9' off of a wall with one head and then
9'
off of a different wall with another head.  The sketches in the Annex (or
Handbook) do a pretty good job showing the different scenarios.

Hope this helps.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
[email protected]
www.fire-design.com

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Friday, September 26, 2014 9:49 AM
To: [email protected]
Subject: RE: Small Room Rule

I've been reading this thread and come to think I've miss understood how
to
apply this exception.

Based on NFPA 13(13ed)Fig A.8.6.3.2.4 I've always thought the only time
you
would exceed the 15'-0" spacing for a sprinkler is when you have a single
sprinkler in a small room.

In a situation where an L shape room 12x18 with a 4' pop out for the entry
in one of the corners along the 18' side, Could you get away with 2
sprinklers or do you need 3?

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to