I want to Thank everyone for the comments. We are all pretty much on the same 
track.
I will continue my discussion with the AHJ.

David L. Smith
Fire Protection Maintenance
City of Lakeland
Public Works / Facilities
228 S. Massachusetts Ave.
Lakeland, Fl. 33801
Office: 863-834-2380
Fax:  863-834-2284
Cell: 863-559-0903
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, October 16, 2014 9:09 AM
To: [email protected]
Subject: RE: Obstructions

Sitting on a plane, so don't have 13 in front of me, but I don't think it meets 
the 3x C or D rule. Seems obstructed to me, at least as I'm seeing it in my 
head.  

Steve 

<div>-------- Original message --------</div><div>From: [email protected] 
</div><div>Date:10/16/2014  5:46 AM  (GMT-08:00) </div><div>To: 
[email protected] </div><div>Subject: RE: Obstructions 
</div><div> </div>Hi David,

My opinion is along the same lines as Tim's.  Also, you can reference the 
picture shown in A.8.5.5.1 of NFPA 13 (2010) which shows the pattern 
development of the sprinkler head.  If you insert your light into this picture 
at 10" below and 6" wide, you can clearly see that you are getting water on 
both sides of the obstruction as stated in A.8.6.5.2.1.4.

                                          Thanks,

Sean Van Gaal
Project Manager
Nicet III Water-Based System Layout #124801
P: (623) 580-7818
C: (602) 400-4512
F: (623) 434-3154
[email protected]

AERO Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ, 85024
(623) 580-7800
aerofire.com




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Thursday, October 16, 2014 5:40 AM
To: [email protected]
Subject: RE: Obstructions

David,
I am referencing NFPA 13, 2010 ed. Chapter 8.6.5.2, Obstructions to sprinkler 
discharge.
If Light or Ordinary Hazard Occupancy you can apply 8.6.5.2.1.4, Structural 
members only. A.8.6.5.2.1.4, discusses that  nonstructural elements are exempt 
but must also comply with "Beam Rule" 8.6.5.1.2 and "Wide Obstruction Rule" 
8.6.5.3.3.

In my opinion based on information you provide below and reviewing NFPA 13 for 
Light and or Ordinary occupancy the sprinkler location is OK. 

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Smith, David L.(FAC)
Sent: Thursday, October 16, 2014 8:18 AM
To: [email protected]
Subject: Obstructions

Good Morning All;

Obstructions, Obstructions, Obstructions; Wow, this is one subject that's worth 
arguing sometimes.

I've been in a discussion on whether a light that is 4' long x 6" wide hanging 
under a sprinkler head less than 18" from the deflector is an obstruction or 
not. (It's right at 10")

Could you all pipe in on what your thoughts are?

David L. Smith
Fire Protection Maintenance
City of Lakeland
Public Works / Facilities
228 S. Massachusetts Ave.
Lakeland, Fl. 33801
Office: 863-834-2380
Fax:  863-834-2284
Cell: 863-559-0903
[email protected]<mailto:[email protected]>



________________________________

PUBLIC RECORDS NOTICE:

All e-mail sent to and received from the City of Lakeland, Florida, including 
e-mail addresses and content, are subject to the provisions of the Florida 
Public Records Law, Florida Statute Chapter 119, and may be subject to 
disclosure.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to