A few things to review: All electrical components are required to be at least 12" off slab. Follow manufacturers installation instructions including grouting of the base plate. Look at the manufacturers dimension drawing provided. It usually requires 1-1/2" of grout under the bottom of the base.
Be careful or the warranty from the manufacturer is voided. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Thomas Reinhardt Sent: Wednesday, November 19, 2014 9:27 AM To: [email protected] Subject: Mounting of Fire Pump Question for the group. Do horizontal fire pumps need to be mounted on a concrete slab? The reason is I had a pump company send me a report with the discrepancy that the pump, when tested vibrated laterally due to the fact that when it was installed they just used a frame bolted to the concrete floor. In researching NFPA 20 I only find some seismic restrictions. Am I missing something? Thanks ________________________________ IMPORTANT NOTICE: This e-mail message is intended to be received only by persons entitled to receive the confidential information it may contain. E-mail messages may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org