NFPA 20, 2013
6.4 Foundation and Setting.
6.4.1* Overhung impeller and impeller between bearings design
pumps and driver shall be mounted on a common
grouted base plate.

6.4.4* The foundation shall be sufficiently substantial to form
a permanent and rigid support for the base plate.


Duane Johnson, PE
Design Manager
Strickland Fire Protection
301-474-1136 Office
301-455-0010 Cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Reinhardt
Sent: Wednesday, November 19, 2014 9:27 AM
To: [email protected]
Subject: Mounting of Fire Pump

Question for the group. Do horizontal fire pumps need to be mounted on a 
concrete slab? The reason is I had a pump company send me a report with the 
discrepancy that the pump, when tested vibrated laterally due to the fact that 
when it was installed they just used a frame bolted to the concrete floor. In 
researching NFPA 20 I only find some seismic restrictions. Am I missing 
something? Thanks


________________________________
IMPORTANT NOTICE: This e-mail message is intended to be received only by 
persons entitled to receive the confidential information it may contain. E-mail 
messages may contain information that is confidential and legally privileged. 
Please do not read, copy, forward, or store this message unless you are an 
intended recipient of it. If you have received this message in error, please 
forward it to the sender and delete it completely from your computer system.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to