IDK about FM.  UFC is clear to me, no you can't use small room - area/density 
only, and no the calcs are not per FM.  There are 5 things you pull from FM and 
only these 5 things, density, design area, hose stream allowance, duration and 
minimum k-factor.  And really these only apply to things defined as HC1-3.  For 
example HPS would follow NFPA 13. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Greg McGahan
Sent: Wednesday, November 19, 2014 10:17 AM
To: [email protected]
Subject: FM Global and the UFC

Does FM allow the "small room rule" for end head pressures in small room rules 
as in NFPA #13?

The UFC is confusing as the installation goes by 13 and the calcs go by FM 
standards.....

Thanks,

Greg McGahan