IDK about FM. UFC is clear to me, no you can't use small room - area/density only, and no the calcs are not per FM. There are 5 things you pull from FM and only these 5 things, density, design area, hose stream allowance, duration and minimum k-factor. And really these only apply to things defined as HC1-3. For example HPS would follow NFPA 13.
Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Wednesday, November 19, 2014 10:17 AM To: [email protected] Subject: FM Global and the UFC Does FM allow the "small room rule" for end head pressures in small room rules as in NFPA #13? The UFC is confusing as the installation goes by 13 and the calcs go by FM standards..... Thanks, Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org