I was referring to the part that says "no less than the size of system
riser, where serving one system riser." and "For multiple system risers
supplied by a manifold, the fire department connection need not be
larger than that for an individual system."
On 11/25/2014 10:25 AM, Tim Stone wrote:
> NFPA  13 is a minimum design /installation Standard, NOT A CODE.
>
> Fire department Pump Trucks are equipped with variable pressure pumps which
> enables the pump operator to increase extra boost when needed.
> I don't see any contradiction.
>  
> Regards,
> G. Tim Stone
>
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Cory Power
> Sent: Tuesday, November 25, 2014 8:39 AM
> To: [email protected]
> Subject: Contradiction if FDC codes? NFPA 13 2013
>
> Could someone explain to me the intent behind this code and if the Annex is
> contradicting?
>
> 8.17.2* Fire Department Connections.
>
> 8.17.2.3* Size. The size of the pipe for the fire department connection
> shall be in accordance with one of the following:
>
> (3) For hydraulically calculated systems, the fire department connection
> shall be permitted to be less than 4 in.
> (100 mm) and no less than the size of system riser, where serving one system
> riser.
>
> A.8.17.2.3 The purpose of a fire department connection is to supplement the
> pressure to an automatic fire sprinkler system.
> It is not the intent to size the fire department connection piping based on
> system demand. For multiple system risers supplied by a manifold, the fire
> department connection need not be larger than that for an individual system.
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> http://www.avast.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to