noun: supplement; plural noun: supplements - something that completes or 
enhances something else when added to it.

How can the possibly pressure be supplemented? Using enough pressure to open 
the FDC check valve will close the valve in the riser. The rule should be 
changed to either calculated or just require a 4" 2-way FDC for everything.

There are buildings in Phoenix with 12 -  2 1/2 " FDC inlets because of an old 
amendment requiring one 2.5" inlet for every 250 gpm system demand. The rule 
was changed when the FD figured out that a pumper truck only carried enough 
equipment to connect to four inlets.
Ron F

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Tuesday, November 25, 2014 6:56 AM
To: [email protected]
Subject: RE: Contradiction if FDC codes? NFPA 13 2013

NFPA  13 is a minimum design /installation Standard, NOT A CODE.

Fire department Pump Trucks are equipped with variable pressure pumps which 
enables the pump operator to increase extra boost when needed.
I don't see any contradiction.
 
Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cory Power
Sent: Tuesday, November 25, 2014 8:39 AM
To: [email protected]
Subject: Contradiction if FDC codes? NFPA 13 2013

Could someone explain to me the intent behind this code and if the Annex is 
contradicting?

8.17.2* Fire Department Connections.

8.17.2.3* Size. The size of the pipe for the fire department connection shall 
be in accordance with one of the following:

(3) For hydraulically calculated systems, the fire department connection shall 
be permitted to be less than 4 in.
(100 mm) and no less than the size of system riser, where serving one system 
riser.

A.8.17.2.3 The purpose of a fire department connection is to supplement the 
pressure to an automatic fire sprinkler system.
It is not the intent to size the fire department connection piping based on 
system demand. For multiple system risers supplied by a manifold, the fire 
department connection need not be larger than that for an individual system.

---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to