I'm a little late to this thread but wanted to remind/advise/warn that Poz-Lok 
was taken out of production and informally recalled pursuant to a class action 
lawsuit that was settled by Northwest Pipe, which acquired the Poz-Lok brand in 
the late 90's.  I use the term "informally recalled" because there was no 
compelling Federal agency or jurisdictional action. Rather, it was a claims 
window that was open for a period of time (two or three years perhaps?) after 
the settlement of this lawsuit.  

Be very careful with this piping; if you don't exactly align and make on that 
cutting washer, you can damage the pipe or create a leaky joint.  This stuff is 
also HYPER prone to corrosion, both from MIC and oxidation.  

These are my recollections from having worked as a technical consultant on the 
lawsuit, which ran was in 1999-2000, I think.   Specific details getty cloudy 
with age, but the lingering conclusion:  bad juju, this stuff.


-----Original Message-----
From: Sprinklerforum on behalf of markloganryan
Sent: Fri 1/9/2015 4:50 PM
To: [email protected]
Subject: RE: Poz lok
 
Thanks a bunch.


Sent from my Verizon Wireless 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Plumbco 
<[email protected]> </div><div>Date:01/09/2015  5:31 PM  (GMT-07:00) 
</div><div>To: [email protected] </div><div>Subject: RE: 
Poz lok </div><div>
</div>
Will take a look on Monday and see what I can find.

Bill Cunningham
Plumbco, Inc.
229 E Peters Rd.
Wenatchee, WA  98801
509-662-0180 Office
509-670-3999 Cell
509-662-1427 Fax

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of markloganryan
Sent: Friday, January 09, 2015 4:21 PM
To: [email protected]
Subject: RE: Poz lok

1" and 1 1/4


Sent from my Verizon Wireless 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Plumbco
<[email protected]> </div><div>Date:01/09/2015  5:04 PM  (GMT-07:00)
</div><div>To: [email protected] </div><div>Subject:
RE: Poz lok </div><div> </div> As I recall it was not copper tube size but
had it's own unique diameter ,
we did have some adaptors 1    1 1/4  and  1 1/2 floating around in our
shop, have not looked at them in years,  what size are you dealing with.


Bill Cunningham
Plumbco, Inc.
229 E Peters Rd.
Wenatchee, WA  98801
509-662-0180 Office
509-670-3999 Cell
509-662-1427 Fax

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of markloganryan
Sent: Friday, January 09, 2015 3:48 PM
To: [email protected]
Subject: RE: Poz lok

I have 9 antifreeze loops that need extended down to the required 5 feet.
Does copper OD match?


Sent from my Verizon Wireless 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Plumbco
<[email protected]> </div><div>Date:01/09/2015  4:40 PM  (GMT-07:00)
</div><div>To: [email protected] </div><div>Subject:
RE: Poz lok </div><div> </div> Poz lok pipe had a different O.D. than Sch10
or 40 pipe, the only way I am aware of connecting to it would require a poz
lok male or female adaptor.
The OD being different would exclude the use of grooved fittings.
We did 1 job with it when it came out years ago and it was a nightmare, the
stuff looked a lot cooler on the vendors display table at a convention than
it did on a job site. How many connections do you need to make?

Bill Cunningham
Plumbco, Inc.
229 E Peters Rd.
Wenatchee, WA  98801
509-662-0180 Office
509-670-3999 Cell
509-662-1427 Fax

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of markloganryan
Sent: Friday, January 09, 2015 3:19 PM
To: [email protected]
Subject: Poz lok

I was hoping to get some information about poz lok. Mainly I was needing
information on transitioning to threaded or grooved pipe. Does the pipe have
the same O.D? Can it be grooved?


Sent from my Verizon Wireless 4G LTE smartphone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to