16.3.1.1 is CMDA sprinklers, not CMSA, unless I am mis-reading your
references. CMDA would just have the 30% increase in the system design
area.
Table 16.3.2.1 (NFPA 13 2013 edition) is the CMSA section. That
includes criteria for a dry pipe system. I am assuming you are able to
use the dry system criteria for your preaction system.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 2/18/2015 2:05 PM, Jamie Seidl wrote:
Hey everyone, I am looking at a freezer project, 30' storage 33' building
height, class II, unencapsulated stored palletized on open shelves. Does NFPA
13 2013 chapter 16 place any restrictions on the use of a pre-action system for
this type of configuration? Specifically I am looking at 16.3.1.1, CMSA with
one level of in rack, per 16.3.1.1, figure e, or f.
Thanks for your input,
Jamie Seidl