16.3.1.1 is CMDA sprinklers, not CMSA, unless I am mis-reading your references. CMDA would just have the 30% increase in the system design area.

Table 16.3.2.1 (NFPA 13 2013 edition) is the CMSA section. That includes criteria for a dry pipe system. I am assuming you are able to use the dry system criteria for your preaction system.