Richard, is it possible that static gage is above a check valve that has
locked in extra pressure, being 20 ft above the floor like that is odd for a
"city" static location, and maybe a 1/2" pr. relief would solve the problem.

(glad you're back), Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Mote
Sent: Tuesday, March 03, 2015 3:34 PM
To: [email protected]
Subject: RE: High Pressure Backflow and Sprinklers

NO fire pump this is what the city water pressure is.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Timothy W Goins
Sent: Tuesday, March 03, 2015 4:12 PM
To: [email protected]
Subject: RE: High Pressure Backflow and Sprinklers

Why not take the suction through the BFP?

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Richard Mote
Sent: Tuesday, March 03, 2015 2:26 PM
To: [email protected]
Subject: RE: High Pressure Backflow and Sprinklers

What I failed to mention, which I realized right after I hit send. The test
hydrant elevation is about 20' above the flange elevation in the building.
My feeling is we need a pressure reducing valve, however the backflow has to
come first so I still need a 184 psi backflow.

Richard Mote CET
Rowe Sprinkler Systems, Inc.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cahill, Christopher
Sent: Tuesday, March 03, 2015 3:09 PM
To: [email protected]
Subject: Re: High Pressure Backflow and Sprinklers

You are at 184 at the floor? As long as the heads are more than 18 ft up you
are good with 175 rating. Hard to get hps with sprinklers much under 18 ft
high so you might be good.

Chris Cahill
Fire Protection Engineer
Burns & McDonnell
[email protected]
952-656-3652 Richard Mote wrote:
Does anyone know of a CMDA Extended coverage sprinkler rated above 175 psi?
Same question for a backflow preventer?
I have looked at all the manufacturers data sheets and I don't see any, but
as sure as I state categorically that there isn't any such animal, someone
will say but what about XXX mfg.
We have a job with a static of 184, residual of 122 and a flow of 1500, want
to use CMDA K14.0 or 25.2, and would like the extra pressure.

Richard Mote CET
Rowe Sprinkler Systems, Inc.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to