You are at 184 at the floor? As long as the heads are more than 18 ft up you 
are good with 175 rating. Hard to get hps with sprinklers much under 18 ft high 
so you might be good.

Chris Cahill
Fire Protection Engineer
Burns & McDonnell
[email protected]
952-656-3652 Richard Mote wrote:
Does anyone know of a CMDA Extended coverage sprinkler rated above 175 psi?
Same question for a backflow preventer?
I have looked at all the manufacturers data sheets and I don't see any, but as 
sure as I state categorically that there isn't any such animal, someone will 
say but what about XXX mfg.
We have a job with a static of 184, residual of 122 and a flow of 1500, want to 
use CMDA K14.0 or 25.2, and would like the extra pressure.

Richard Mote CET
Rowe Sprinkler Systems, Inc.