I have put sway bracing on the branch lines to offload the bracing on the main. I believe Ken Wagoner is "on the road" today, but hopefully he will chime in for the best solution to this.

I have run into this situation, or similar. Even if you brace between every branch line on the main, the weight of the branchline + main exceeds the values allowed for the type of pipe and spacing. So, in order to reduce the weight on the main bracing, I will put a seismic brace (not just a restraint) about 30' intervals along the branch line. My rationale is that the cross main brace/pipe is no longer carrying that load. I hope it is correct. The AHJs I have worked with have accepted this manner.

An alternative answer would be to upsize the main. I know it is not ideal, but with the way we have to deal with bracing, that may end up being your only option if my idea above is not in correct compliance with NFPA 13.

Again, though, Ken will be the one to likely have the best answer.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 3/12/2015 8:53 AM, Jerry Van Kolken wrote:
I've run into this issue before and still not sure how to handle it. What do
you do when your figuring out the brace calculations and a single branchline
will exceed the valves in NFPA -13 9.3.5.5.2? and 2 branchlines will put you
off the charts.

I have a 2.5" main and a single branchline weights 423 lbs.

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to