You need to add longitudinal  braces to your branch lines...... after
Longitudinal braces are added to the branch lines you no longer need to
include the branch lines weights into your lateral main calculations.  

Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906

[email protected]
www.norcalfire.com

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Thursday, March 12, 2015 8:53 AM
To: [email protected]
Subject: Bracing with heavy Branchlines

I've run into this issue before and still not sure how to handle it. What do
you do when your figuring out the brace calculations and a single branchline
will exceed the valves in NFPA -13 9.3.5.5.2? and 2 branchlines will put you
off the charts.

 

I have a 2.5" main and a single branchline weights 423 lbs. 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to