Table 16.2.3.1 for 25' storage height & 32' ceiling specifies either 14.0k or 16.8k heads.
Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Wednesday, March 18, 2015 2:44 PM To: [email protected] Subject: Re: ESFR & Storage Why wouldn’t you use the K-25 and apply 20 psi? Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Mar 18, 2015, at 8:04 AM, Brian Harris <[email protected]> wrote: > > Excuse me if this is a dumb question but I'm doing a large warehouse that > falls under table 16.2.3.1 (2007) with 25' storage & max ceiling of 32'. > Looks like I can use either 14.0k or 16.8k heads. What's the reason I > couldn't use the 25.2K heads and save on end head pressure? > > Brian Harris, CET > BVS Systems Inc. > Sprinkler Division > bvssystemsinc.com<http://bvssystemsinc.com/> > Phone: 704.896.9989 > Fax: 704.896.1935 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org