Early ESFR tests FYI:

http://www.iafss.org/publications/fss/5/877/view

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, March 18, 2015 2:07 PM
To: [email protected]
Subject: Re: ESFR & Storage

DING DING DING.  We have a winner.

Historically ESFR has no limit on clearance.  It is simply an Up to on
Ceiling height and up to on storage height.  Anything below the two maximums
is applicable.  That is how the criteria is still applied but behind the
scenes clearance has become an issue (as to whether the allowance is allowed
in the standard aka it applies to both new criteria being added or existing
criteria being allowed to remain.)


Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 18, 2015, at 11:59 AM, Matt Grise <[email protected]> wrote:
> 
> You can use the criteria for 35' max ceiling height - since 32' is less
than the max allowed.
> 
> Matt Grisé PE*, LEED AP, NICET II  
> Sales Engineer 
> Alliance Fire Protection 
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO 
>  
> 913.888.0647 ph 
> 913.888.0618 f 
> 913.927.0222 cell 
> www. AFPsprink.com 
>  
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Brian
Harris
> Sent: Wednesday, March 18, 2015 1:59 PM
> To: [email protected]
> Subject: RE: ESFR & Storage
> 
> Table 16.2.3.1 for 25' storage height & 32' ceiling specifies either 14.0k
or 16.8k heads.
> 
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> 
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Roland
Huggins
> Sent: Wednesday, March 18, 2015 2:44 PM
> To: [email protected]
> Subject: Re: ESFR & Storage
> 
> Why wouldnÂ’t you use the K-25 and apply 20 psi?
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
> 
> 
> 
> 
> 
>> On Mar 18, 2015, at 8:04 AM, Brian Harris <[email protected]>
wrote:
>> 
>> Excuse me if this is a dumb question but I'm doing a large warehouse that
falls under table 16.2.3.1 (2007) with 25' storage & max ceiling of 32'.
Looks like I can use either 14.0k or 16.8k heads. What's the reason I
couldn't use the 25.2K heads and save on end head pressure?
>> 
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://bvssystemsinc.com/>
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to