Hi Bill,

 

Hmmm, wait until after the fire ?, not me. 

 

Here are the EXACT definitions and stipulations from the 2015 IBC that
apply;

 

702 FIRE WALL. A fire-resistance-rated wall having protected openings, which
restricts the spread of fire and extends continuously from the foundation to
or through the roof, with sufficient structural stability under fire
conditions to allow collapse of construction on either side without collapse
of the wall.

 

706.1.1 Party walls. Any wall located on a lot line between adjacent
buildings, which is used or adapted for joint service between the two
buildings, shall be constructed as a fire wall in accordance with
Section706. Party walls shall be constructed without openings and shall
create separate buildings.

 

706.3 Materials. Fire walls shall be of any approved noncombustible
materials. Exception: Buildings of Type V construction.

 

714.1 Scope. The provisions of this section shall govern the materials and
methods of construction used to protect through penetrations and membrane
penetrations of horizontal assemblies and fire-resistance-rated wall
assemblies.

 

714.3 Fire-resistance-rated walls. Penetrations into or through fire walls,
fire barriers, smoke barrier walls and fire partitions shall comply with

Sections714.3.1 through 714.3.3.

 

714.3.1 Through penetrations. Through penetrations of fire-resistance-rated
walls shall comply with Section714.3.1.1or 714.3.1.2.

 

714.3.1.1 Fire-resistance-rated assemblies. Penetrations shall be installed
as tested in an approved fire-resistance-rated assembly.

 

714.3.1.2 Through-penetration firestop system. Through penetrations shall be
protected by an approved penetration firestop system installed as tested in
accordance with ASTM E 814 or UL 1479, with a minimum positive pressure
differential of 0.01 inch (2.49 Pa) of water and shall have an F rating of
not less than the required fire-resistance rating of the wall penetrated.

 

So, a designer will need to demonstrate a tested/listed system for the
penetrating items for the specific application.  Another issue to consider
with Party Walls, since a party wall sits on a lot line and thus in addition
to creating separate buildings also creates separate lots.  With that said
individual property ownership issues could necessitate an easement, so
ownership issues may need to be considered.

 

Bill to answer your question it's the Missouri thing..show me, not just
that's it permitted by code but how.  

 

Hope this helps,

 

John

 

 

John Drucker, CET

Assistant Construction Official

Fire Protection Subcode Official

Building/Fire/Electrical Inspector

Borough of Red Bank

Red Bank, New Jersey

Email: [email protected] <mailto:[email protected]> 

Cell/Text: 732-904-6823

 

 

 

 

 

 

 

 

 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bill Brooks
Sent: Thursday, March 26, 2015 3:19 PM
To: [email protected]
Subject: Fire Wall Integrity

 

John, now that you bring up the subject of collapse on both sides, just how
do you treat this subject?  I have seen the interpretation which appears to
suggest that a sprinkler pipe penetration of a fire wall would not be
acceptable if the pipe (in coming down with collapsing side) somehow
compromised the gypsumboard separation assembly.  Same with an electrical
conduit.  I'm also not sure how to design the collapsing side in such a way
that it falls cleanly to the ground without some member shifting sideways
and penetrating the separating assembly.

 

In other words, do you wait till after the fire to say it works or doesn't
work?

 

Bill Brooks

 

-----Original Message-----

From: Sprinklerforum [
<mailto:[email protected]>
mailto:[email protected]]

On Behalf Of John Drucker

Sent: Wednesday, March 25, 2015 6:10 AM

To:  <mailto:[email protected]>
[email protected]

Subject: Re: Floor Control Stations

 

LOL Horizontal Fire Wall......we inspectors are still scratching our heads
how this meets the performance definition of a firewall...collapse on one
side, stays in place....then again sprinkler guys are famous for skyhooks.

You just can't make this stuff up.

 

John Drucker - Mobile Email

 <mailto:[email protected]%3cmailto:[email protected]>
[email protected]<mailto:[email protected]>

Cell/Text 732-904-6823

 

 

"rongreenman ." < <mailto:[email protected]> [email protected]>
wrote:

 

Roland,

 

Would you think with all the hoopla about non-combustible floor assemblies
being equivalent to horizontal fire walls. and high rises typically not
needing vertical fire separation, that a floor would fit a loose definition
of a zone? Two floors, even if within the area limits of a single system
seem to define two zones. Just thinking, and remember that Leyton was
concerned this morning that my meds have lost their efficacy, so I may just
be having another flashback to the sixties.

 

 

On Tue, Mar 24, 2015 at 12:00 PM, David Blackwell <
<mailto:[email protected]> [email protected]> wrote:

 

> On a related note and of interest to this forum should be the change 

> to next section, IFC 914.3.1.2, in the 2015 edition.  The limiting 

> phrase "In buildings that are more than 420 feet (128m) in building 

> height," has been added to the 2015 edition published by ICC.  Prior 

> to that change, the 2012 edition applied the separate supply piping 

> requirement per IFC 914.3.1.2 more broadly to include high-rise 

> buildings

below that height.

> 

> Respectfully,

> 

> 

> David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 

> State Fire Marshal SC Department of Labor, Licensing, & Regulation,

> 141 Monticello Trail, Columbia, SC 29203

> Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]

> Fax: 803.896.9806 [Office]

> Email:    <mailto:[email protected]> [email protected]

> Website:   <http://www.scfiremarshal.llronline.com/>
http://www.scfiremarshal.llronline.com/

> 

> 

> Please note that you can sign up to receive automatic information on 

> SC Division of Fire and Life Safety current events, policies, laws and 

> procedures by visiting our Web site at:

>  <http://www.scfiremarshal.llronline.com/>
http://www.scfiremarshal.llronline.com/

> 

> 

> -----Original Message-----

> From: Sprinklerforum [mailto:

>  <mailto:[email protected]>
[email protected]] On Behalf Of Roland 

> Huggins

> Sent: Tuesday, March 24, 2015 2:45 PM

> To:  <mailto:[email protected]>
[email protected]

> Subject: Re: Floor Control Stations

> 

> The main point is that for standard high rises, the codes and 

> standards only require a single riser.

> 

> Very Tall High Rises (>420 ft) are a unique beast.  The IFC requires 

> these tall buildings to have 2 risers per zone.  Not 100% sure but I 

> don't think they mean each floor is a zone.  The same section says 

> "Each riser shall supply sprinklers on alternate floors".  A lot of 

> these building going up in parts of the Middle East but not hearing about
any here in the USA.

Any

> one involved with one?

> 

> Roland

> 

> 

> Roland Huggins, PE - VP Engineering

> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives

> Dallas, TX

>  <http://www.firesprinkler.org> http://www.firesprinkler.org <
<http://www.firesprinkler.org/> http://www.firesprinkler.org/>

> 

> 

> 

> 

> 

> > On Mar 20, 2015, at 9:55 AM, David Blackwell

< <mailto:[email protected]> [email protected]>

> wrote:

> >

> > It is also found in Section 914.3.1.1 of the 2012 IFC, which is

> referenced from 2012 IFC Table 903.2.11.6 [Additional Required Fire 

> Suppression Systems].

> >

> > Respectfully,

> >

> >

> > David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 

> > State Fire Marshal SC Department of Labor, Licensing, & Regulation,

> > 141 Monticello Trail, Columbia, SC 29203

> > Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]

> > Fax: 803.896.9806 [Office]

> > Email:    <mailto:[email protected]> [email protected]

> > Website:   <http://www.scfiremarshal.llronline.com/>
http://www.scfiremarshal.llronline.com/

> >

> >

> > Please note that you can sign up to receive automatic information on 

> > SC Division of Fire and Life Safety current events, policies, laws 

> > and procedures by visiting our Web site at:

> >  <http://www.scfiremarshal.llronline.com/>
http://www.scfiremarshal.llronline.com/

> >

> > -----Original Message-----

> > From: Sprinklerforum

> > [ <mailto:[email protected]>
mailto:[email protected]] On Behalf Of 

> > Fairchild, Jack

> > Sent: Friday, March 20, 2015 12:15 PM

> > To:  <mailto:[email protected]>
[email protected]

> > Subject: RE: Floor Control Stations

> >

> > IBC 2009/2012  -  403.3.1  Buildings in excess of 420 feet in height.

> >

> > Jack Fairchild

> >

> >

> > -----Original Message-----

> > From: Sprinklerforum

> > [ <mailto:[email protected]>
mailto:[email protected]] On Behalf Of 

> > Dale Wingard

> > Sent: Friday, March 20, 2015 11:45 AM

> > To: '[email protected]'

> > Subject: RE: Floor Control Stations

> >

> > Jeremy,

> >

> > I believe that is just a Marriott requirement.

> >

> > Dale F. Wingard  SET

> >

> >

> >

> > -----Original Message-----

> > From: Sprinklerforum

> > [ <mailto:[email protected]>
mailto:[email protected]] On Behalf Of 

> > Jeremy Frazier

> > Sent: Friday, March 20, 2015 10:38 AM

> > To:  <mailto:[email protected]>
[email protected]

> > Subject: Floor Control Stations

> >

> > Where in NFPA/IBC does it say that if you have 2 standpipes, your 

> > sprinkler system should connect to both standpipes?  I've looked 

> > through 14 (2010),13

> > (2010) and IBC (2009)  and I have not found anything requiring it.  

> > Is

> this one of those things like electrical rooms with 2 penetrations or 

> is there and actual code?

> >

> >

> >

> >

> >

> > Jeremy Frazier

> >

> > P:571-931-1004

> > F:571-931-1010

> >

> >

> >

> > _______________________________________________

> > Sprinklerforum mailing list

> >  <mailto:[email protected]>
[email protected]

> >  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin

> > kl er.org _______________________________________________

> > Sprinklerforum mailing list

> >  <mailto:[email protected]>
[email protected]

> >  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin

> > kl

> > er.org

> >

> > _______________________________________________

> > Sprinklerforum mailing list

> >  <mailto:[email protected]>
[email protected]

> >  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin

> > kl er.org _______________________________________________

> > Sprinklerforum mailing list

> >  <mailto:[email protected]>
[email protected]

> >  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin

> > kl

> > er.org

> 

> _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]>
[email protected]

> 

> 

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]>
[email protected]

> 

> 

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> 

 

 

 

--

Ron Greenman

Instructor

Fire Protection Engineering Technology

Bates Technical College

1101 So. Yakima Ave.

Tacoma, WA 98405

 

 <mailto:[email protected]> [email protected]

 

 <http://www.bates.ctc.edu/fireprotection/>
http://www.bates.ctc.edu/fireprotection/

 

253.680.7346

253.576.9700 (cell)

 

Member:

ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

 

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

 

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]>
[email protected]

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]>
[email protected]

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]>
[email protected]

 
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to