Now does that mean all three or the requisite two? I believe you stated the
third was a back-up should one or the other of the primary pumps be down
for service.

On Fri, Mar 27, 2015 at 9:47 AM, Travis Mack <[email protected]> wrote:

> We did just get directed to the following section from NFPA 20, 2010
> edition that explicitly addresses this:
>
> 14.2.5.2.3.1 Where simultaneous operation of multiple pumps is possible or
> required as part of a system design, the acceptance test shall include a
> flow test of all pumps operating simultaneously.
>
> So, it looks like the EOR will be looking to re-design a few of the
> components.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 3/26/2015 1:32 PM, [email protected] wrote:
>
>> With 3 pumps, 2 needed and one backup the suction and discharge header
>> should be sized for 2 pumps. 16" pipe would result in a suction velocity of
>> less than 10 fps, I believe that is the recommended limit in NFPA 20. All
>> common pipe subject to the full flow of two pumps should be sized
>> accordingly.
>> Ron F
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected].
>> org] On Behalf Of Travis Mack
>> Sent: Thursday, March 26, 2015 12:25 PM
>> To: [email protected]
>> Subject: Large pumping capacity
>>
>> I am working on a project where there is a fairly large demand.  The EOR
>> has determined there are to be (3) 3000 gpm pumps.  These are all installed
>> parallel.  One of the pumps is to be a backup pump. The design has not been
>> finalized, but the system demand (overhead sprinklers and grate foam
>> nozzles) is somewhere around 6000 gpm. That is why we have two 3000 gpm
>> pumps in parallel to create a 6000 gpm pumping capacity.
>> There were some errors in the EOR pump room design that led to a few
>> other questions.  We are getting conflicting information from the EOR and
>> the pump guys.  The arrangement is that the pumps share a common suction
>> header and a common discharge header.
>>
>> Per NFPA 20, a 3000 gpm pump needs a 12" discharge.  The EOR showed 10"
>> discharge piping and equipment, so this is what flagged some questions
>> with the pump room design.  The questions are now:
>>
>> 1 - Should the test header be sized to accommodate a 6000 gpm pump, or a
>> 3000 gpm pump?  The pump guy says that the common discharge header must
>> be sized for the combined pumping capacity.  The EOR states that it is only
>> based on 1 pump flowing.  I seem to agree with the pump guy, in that you
>> need to test with both pumps flowing so you can test your water supply as
>> well to show you can get the full 150% flow from the water supply.  It is
>> easy to size the piping so that the recommended velocities in NFPA 20 are
>> not exceeded.  It is just a question as to what is the basis.
>>
>> 2 - Should the common discharge header that the pumps tie in to be sized
>> based on 3000 gpm pump or 6000 gpm pump?  I believe that the common piping
>> (after the pump discharge valve) only needs to be sized based on hydraulic
>> calculations.
>>
>> 3 - These are diesel pumps.  The individual relief valves are tied into a
>> common discharge header.  How should this be sized?  Based on 3000 or
>> 6000 gpm pumps?
>>
>> We are awaiting input from the authority having jurisdiction as well on
>> this topic.  The biggest issue is the pump test header and relief valve
>> discharge piping.  There are more issues of now trying to fit 12"
>> valves/pipe/fittings on the discharge side of a pump in a room that was
>> tight to begin with and was designed for 10" discharge equipment.
>>
>> Part of the issue is that NFPA 20 only goes to 5000 gpm tables for sizing
>> pump room piping/equipment.  The EOR is stating that the NICET tech is to
>> correct anything in the pump room and provide it per NFPA 20.  However,
>> since we have a 6000 gpm total capacity, it is not possible to size things
>> based on the summary table in NFPA 20 if it is to be based on 6000 gpm.
>>
>> I am just interested as to the thoughts of the guys on this forum.
>>
>> --
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to