What Reed said.

On Wed, Apr 22, 2015 at 9:28 AM, Reed A. Roisum, SET <[email protected]>
wrote:

> 2012 IFC, 905.3.1 Height.  Class III standpipe systems shall be installed
> throughout buildings where the floor level of the highest story is located
> more than 30 feet above the lowest level of the FD vehicle access...
>
> There is nothing about the "story" being occupied or not so I believe you
> have to count the mezzanine.  Actually, Figure 905.3.1(1) in the IFC shows
> a section with the dimension line drawn to a floor labeled "Mezzanine" and
> a note that says "Highest Floor Level of Highest Story".
>
> The commentary states this also, "The threshold based on the height of the
> building is independent of the occupancy of the building, the area of the
> building or the presence of an automatic sprinkler system.  This is based
> on the universal need to be able to provide a water supply for fire
> suppression in any building and on the limitations of the physical effort
> necessary to extend hose lines vertically."
>
>
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
> http://www.kfiengineers.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Travis Mack
> Sent: Wednesday, April 22, 2015 10:38 AM
> To: <[email protected]>
> Subject: Standpipes
>
> Does a loft/mezzanine count toward the height to require a standpipe?
>
> Example: 4th floor is 29'-4" above lowest level of fire department access.
> So standpipe would not be required.
>
> But these units have a loft/mezzanine that will be obviously above the
> 30'. The only way to access the loft is from a stair in the unit on the
> fourth floor.
>
> So standpipes yes or no? It is an R-2 occupancy.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to