Doesn't NFPA 14 require standpipe isolation valves? How can you individually
isolate the standpipes in the scenario you describe. The valve that controls #1
would also control #2&3. That doesn't seem to correlate with a requirement to
be able to individually isolate each standpipe.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
> On Aug 21, 2015, at 6:47 AM, Justin Petcosky <[email protected]>
> wrote:
>
> We have an engineer on a project that wants to run 2- Manuel wet standpipes
> off the 1st floor sprinkler zone (which is supplied by a combination riser /
> standpipe). So another words the combination riser comes from the basement of
> the building which supplies the sprinkler zones. Then off the first floor
> sprinkler zone the engineer wants to pick up two additional stairwells. I
> know this isn't standard practice but please point me in the right direction
> in NFPA 14.
>
>
>
>
> Justin Petcosky
> Vice President
> Petcosky and Sons
> Plumbing, HVAC and Fire Protection
> 421 Commerce Rd.
> Vestal, NY 13850
> www.petcosky-sons.com<http://www.petcosky-sons.com/>
> 607-797-0160 Ext.105
> [logo1]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org