Working pressure is defined, and used in a few places in the text. Operating
Pressure is not defined but is used extensively and is obviously meant to be
used to calculate the discharge rate of sprinkler heads. According to
Webster's, Working and Operating are synonymous, but this results in a
problem where ~minimum operating pressure (for sprinklers) shall be 7 psi~,
due to the "2nd head phenomena", where the Pv between the end and 2nd heads
exceeds the Pf, making Pn at the 2nd head less than 7 psi. Since only the Pn
produces flow at the 2nd head we are "allowed" to subtract Pv.

 

So the suggestion for the definition of Operating Pressure regarding
sprinkler discharge is to specify minimum Pn shall be 7 psi.

 

Just wanted to get that off my chest.

 

thanks,

 

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org