Since other than NFPA 15 systems, virtually NO ONE applies Pv so why add the 
additional complexity.  This is especially true with Pt being a MORE 
conservative approach.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 24, 2015, at 8:11 AM, Brad Casterline <[email protected]> wrote:
> 
> Working pressure is defined, and used in a few places in the text. Operating
> Pressure is not defined but is used extensively and is obviously meant to be
> used to calculate the discharge rate of sprinkler heads. According to
> Webster's, Working and Operating are synonymous, but this results in a
> problem where ~minimum operating pressure (for sprinklers) shall be 7 psi~,
> due to the "2nd head phenomena", where the Pv between the end and 2nd heads
> exceeds the Pf, making Pn at the 2nd head less than 7 psi. Since only the Pn
> produces flow at the 2nd head we are "allowed" to subtract Pv.
> 
> 
> 
> So the suggestion for the definition of Operating Pressure regarding
> sprinkler discharge is to specify minimum Pn shall be 7 psi.
> 
> 
> 
> Just wanted to get that off my chest.
> 
> 
> 
> thanks,
> 
> 
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to