Thanks Craig.  I agree that this will require to be calc'ed for Group A 
Plastic.  I was hoping to find some type of substantiation for the 
interpretation that I read.  So onward and upward with making the system flow.

Thank you, 
Bob Knight, CET III 
208-318-3057 

--- [email protected] wrote:

From: <[email protected]>
To: <[email protected]>
Subject: RE: VHS Archive Storage
Date: Tue, 12 May 2015 20:36:46 +0000

The tape material is PET and the cases are unexpanded polystyrene.  Both are 
listed in NFPA 13 as Group A plastics.

In one section of NFPA 13, the magnetic tape alone is listed as a Class IV 
commodity but that does not include the casing of a VHS or cassette tape.



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, May 12, 2015 1:19 PM
To: [email protected]
Subject: VHS Archive Storage

I have a small room (538 sf) that is being used for VHS Archive Storage.  I 
read an interpretation that says that the VHS tapes can be considered Class IV 
rather than Group A plastics.  I can't find anything in 13, 232, IBC, or IFC 
that corroborates this.  Can anyone
verify  this   or  give  me  direction?  This is in an existing
sprinklered building that was originally calc'ed for LH.  Somewhere over the 
years the area was converted from a small library that was open to a common 
office area to a closed off compartment.  Any help will be appreciated.
Thank you,

Bob Knight, CET III

208-318-3057

www.firebyknight.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to