3.3.5 Ceiling Types.
3.3.5.1 Flat Ceiling.    A continuous ceiling in a single plane.

I don't think anyone would look into the room you're describing and say
"hey look at that flat ceiling!".



On Wed, Jul 15, 2015 at 10:30 AM, Brian Harris <[email protected]>
wrote:

> I think the key is the 36" vertical change.
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, July 15, 2015 1:20 PM
> To: [email protected]
> Subject: RE: ceilings with varying degrees of slope
>
> That's what we were thinking, but the figures show a flat, level ceiling,
> whereas ours were curved. We were hesitant to make that jump in
> interpreting sloping vs. flat concept.
>
> Ed
> Aero
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Wednesday, July 15, 2015 9:54 AM
> To: [email protected]
> Subject: RE: ceilings with varying degrees of slope
>
> Take a look at 8.8.4.1.1.4 (2007), you should be fine so long as you don't
> start getting into unprotected ceiling pockets....
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, July 15, 2015 12:52 PM
> To: [email protected]
> Subject: RE: ceilings with varying degrees of slope
>
> It's about 15 inches
>
> Ed
> Aero Automatic Sprinkler
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Wednesday, July 15, 2015 9:49 AM
> To: [email protected]
> Subject: RE: ceilings with varying degrees of slope
>
> What's the difference in vertical height between the "flat" ceiling and
> the high point of the "curved" ceiling?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Wednesday, July 15, 2015 12:33 PM
> To: [email protected]
> Subject: ceilings with varying degrees of slope
>
> Good morning all,
> We have a situation where there are multiple sections of ceilings that
> start off flat/level for several feet and then curve upwards with a pitch
> that will exceed 2:12 at some point in the curve. This situation occurs in
> a repeating pattern over a large section of floor area. At the top of the
> curve there is a small slot that serves as a return air opening. The design
> intent was to use concealed, quick response, ordinary hazard, extended
> coverage sprinklers located in the flat part of the ceiling. The question
> is "this a flat ceiling?". Does the portion of the ceiling that exceeds
> 2:12 nullify the use of the flat ceiling design?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to