Tom/ Travis,

Thanks this is exactly what I was thinking but wanted another opinion.

Best Regards,

Spencer Allen


-----Original Message-----
From: Tom Wellen [mailto:[email protected]] 
Sent: 15 September 2015 16:46
To: [email protected]
Subject: Re: Galv Pipe on Dry System

Informal Interpretations
Subject:         Galvanized Pipe Requirement for Dry Systems 
Date:    9/3/10
Summary:         You asked the following question: ?Does section 8.4.7.2.1
mean that all dry systems now have to have galvanized pipe above the dry
valve or is it only limited to Control Mode Specific Application (CMSA)
(large drop) sprinklers?? In response to your question, we have reviewed
NFPA 13, 2010 Edition as the applicable standard. Our informal
interpretation is that internally galvanized steel is not required on dry
pipe and preaction systems using other than CMSA (large drop) sprinklers and
other situations noted below. 

Section 8.4.7 of NFPA 13 addresses special requirements for CMSA (large
drop) sprinklers. Section 8.4.7.1 and 8.4.7.2.1 are subsections of 8.4.7 and
set requirements that only apply to the use of large drop sprinklers and do
not apply to any other sprinkler types. Thus, NFPA 13 does not require
galvanized pipe for all dry pipe and preaction systems. There is some
misconception that all dry pipe and preaction systems are required to have
galvanized piping. Dry pipe and preaction systems can be black steel except
for a few applications. The dry pipe and preaction system piping must be
corrosion resistant or internally galvanized when small orifice K-factor 4.2
sprinklers protect light hazard occupancies according to Section 8.3.4.3.
Water-cooling towers under the Special Occupancy Requirements Chapter in
Section 21.21.2.10.1 requires the piping, fittings, hangers, braces, and
attachment hardware including fasteners shall be hot-dip galvanized steel or
use other materials that have a superior corrosion resistance. Two other
sections that require galvanized pipe are Section 6.9.3.3 that requires all
piping to water motor-operated devices shall be galvanized or brass or other
corrosion-resistant material acceptable under this standard, and Section
6.9.3.4 that piping between the sprinkler system and a pressure-actuated
alarm-initiating device shall be galvanized or of nonferrous metal or other
approved corrosion-resistant material. Thus, there is no carte blanche
requirement that all dry pipe and preaction systems must have galvanized
piping.


Standard:        1313
Paragraph:       8.4.78.4.7.2.1
Edition:         2010



> On Sep 15, 2015, at 10:36 AM, Spencer Allen <[email protected]>
wrote:
> 
> Ladies and Gents,
> 
> 
> 
> Is there a clause within NFPA that requires the use of galv pipe on 
> dry systems?  The only clause I can find is 8.4.7.2 and this is in 
> reference to CMSA sprinklers.
> 
> 
> 
> Thanks in advance,
> 
> Spencer Allen
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to