Just for discussion, look at 8.12.5.1.1. Isn't that essentially a cross section of a baffle? While not specifically having a section dedicated to baffles for ESFR as other sprinklers types do, and allowing spacing's less than 8'-0, what would you do if you had a solid structural beam? Section 8.12.5.1.2 says that you can ignore the beam if you have a sprinkler on each side of the beam. I am willing to bet there is a chance those (2) sprinklers end up closer than 8'-0 in a lot of cases. How is this any different than a baffle, it serves the same purpose? Section 8.12.5.1.2 also does not apply and conditions or restrictions when placing a sprinkler on each side. Am I missing something?
Eric V. Tysinger Designer Wiginton Fire Systems - Miami, FL Email: [email protected] Main: 305-888-2402 Direct: 305-830-0490 Fax: 305-888-3804 Mobile: 239-633-9703 Confidentiality Notice: This e-mail message, including any attachments, is for the sole use of the intended recipients and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Tuesday, September 15, 2015 8:42 PM To: [email protected] Subject: Re: ESFR Sprinklers and Baffles By spacing them at no less than 8 ft. No being a SA (well too much of one) but that is simply one of the annoying limits on ESFR. If close to 8 ft, try a staggered pattern (like often seen in days gone by). Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Sep 15, 2015, at 5:31 AM, Lamar Vaughn <[email protected]> wrote: > > I need some help with this, I find in NFPA 13 (2013) chapter 8 > acceptable ways to use baffles between close spaced heads but do not > find this language with regard to ESFR sprinklers. Is it not > acceptable to use baffles on these heads? And if not, how do you deal with > less than 8 ft. > spacing? Thanks for your input. > > Lamar Vaughn, SET > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org