Even when using obstructions per 8.12.5.1.1 as baffles, the minimum
protected area per sprinkler must not violate section 8.12.2.3.
Met vriendelijke groet / Best regards,
Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112
At 08:58 16-9-2015 -0400, you wrote:
Just for discussion, look at 8.12.5.1.1. Isn't that essentially a
cross section of a baffle? While not specifically having a section
dedicated to baffles for ESFR as other sprinklers types do, and
allowing spacing's less than 8'-0, what would you do if you had a
solid structural beam? Section 8.12.5.1.2 says that you can ignore
the beam if you have a sprinkler on each side of the beam. I am
willing to bet there is a chance those (2) sprinklers end up closer
than 8'-0 in a lot of cases. How is this any different than a
baffle, it serves the same purpose? Section 8.12.5.1.2 also does not
apply and conditions or restrictions when placing a sprinkler on
each side. Am I missing something?
Eric V. Tysinger
Designer
Wiginton Fire Systems - Miami, FL
Email: [email protected]
Main: 305-888-2402
Direct: 305-830-0490
Fax: 305-888-3804
Mobile: 239-633-9703
Confidentiality Notice:
This e-mail message, including any attachments, is for the sole use
of the intended recipients and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient,
please contact the sender by reply e-mail and destroy all copies of
the original message.
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Roland Huggins
Sent: Tuesday, September 15, 2015 8:42 PM
To: [email protected]
Subject: Re: ESFR Sprinklers and Baffles
By spacing them at no less than 8 ft. No being a SA (well too much
of one) but that is simply one of the annoying limits on ESFR. If
close to 8 ft, try a staggered pattern (like often seen in days gone by).
Roland
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
> On Sep 15, 2015, at 5:31 AM, Lamar Vaughn <[email protected]> wrote:
>
> I need some help with this, I find in NFPA 13 (2013) chapter 8
> acceptable ways to use baffles between close spaced heads but do not
> find this language with regard to ESFR sprinklers. Is it not
> acceptable to use baffles on these heads? And if not, how do you
deal with less than 8 ft.
> spacing? Thanks for your input.
>
> Lamar Vaughn, SET