Thought so, thanks!

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Friday, September 18, 2015 4:01 PM
To: [email protected]
Subject: Re: Pump Rating

If the total head is given in feet then yes.  If it is given in PSI, then no.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 9/18/2015 1:00 PM, Brian Harris wrote:
> I have a pump data sheet that says the pump capacity is 500 gpm & the total 
> head is 91 psi. Isn't that considered what the pump is rated for? I'm being 
> told that you have to multiply the total head by .434 which gives you 39.5 
> psi. Which is right?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>