Thought so, thanks! Brian Harris, CET BVS Systems Inc. bvssytemsinc.com
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Friday, September 18, 2015 4:01 PM To: [email protected] Subject: Re: Pump Rating If the total head is given in feet then yes. If it is given in PSI, then no. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 9/18/2015 1:00 PM, Brian Harris wrote: > I have a pump data sheet that says the pump capacity is 500 gpm & the total > head is 91 psi. Isn't that considered what the pump is rated for? I'm being > told that you have to multiply the total head by .434 which gives you 39.5 > psi. Which is right? > > Brian Harris, CET > BVS Systems Inc. > Sprinkler Division > bvssystemsinc.com<http://bvssystemsinc.com/> > Phone: 704.896.9989 > Fax: 704.896.1935 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org