The schematic that you are remembering might be Figure A.4.20.1.2(b) of NFPA 20-2013, which shows a FDC downstream of all of the control valves and check valves associated with the fire pump installation.
Larry Keeping -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: September-25-15 9:48 AM To: [email protected] Subject: RE: FDC on Fire Pump For some reason I thought I remembered seeing a schematic but apparently not. So as long as the FDC ties into the pump discharge downstream of the discharge check valve I'm good to go correct? Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, September 25, 2015 9:41 AM To: [email protected] Subject: RE: FDC on Fire Pump 13 (2013) 8.17.2.4.8 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Friday, September 25, 2015 6:40 AM To: [email protected] Subject: FDC on Fire Pump Glad its Friday but I must be having a brain cramp..... Where does it specify where the FDC ties into the pump discharge? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org