What happens when the fire department pumps into the FDC with more than the 
normal street pressure and over pressurizes the system?
I think that you would need to separate the FDC from the city supply. 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Friday, September 25, 2015 8:36 AM
To: [email protected]
Subject: Re: FDC on Fire Pump

Devil's advocate. The code says there can be not control valve in the FDC line 
(itself). It also has to be downstream of the check valve that separates the 
source from the system so you don't pump a loop back to the pumper. I don't 
recall off the top of my head anything that says you have to be able to isolate 
the pump without effecting the FDC but I'll buy Ed's statement since I can't 
refute it without actually opening a book and it just makes sense. But lets 
assume a vault in the yard with a DCVA, PIV and FDC tied in after the last 
control valve there, then say 200 ft of UG to a pump with a by-pass loop and 
then to a manifold with five risers. Then take the pump out completely and tell 
me what's different than the place next door without a pump. In the first 
example do I have to run that FDC line 200' extra feet to tie it in after the 
pump but not do the same on the place with no pump?

On Fri, Sep 25, 2015 at 8:22 AM, Brian Harris <[email protected]>
wrote:

> Sounds nice but I only have the 2007 edition.....
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Larry 
> Keeping
> Sent: Friday, September 25, 2015 10:49 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> The schematic that you are remembering might be Figure A.4.20.1.2(b) 
> of NFPA 20-2013, which shows a FDC downstream of all of the control 
> valves and check valves associated with the fire pump installation.
>
> Larry Keeping
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian 
> Harris
> Sent: September-25-15 9:48 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> For some reason I thought I remembered seeing a schematic but 
> apparently not. So as long as the FDC ties into the pump discharge 
> downstream of the discharge check valve I'm good to go correct?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of 
> [email protected]
> Sent: Friday, September 25, 2015 9:41 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> 13 (2013) 8.17.2.4.8
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian 
> Harris
> Sent: Friday, September 25, 2015 6:40 AM
> To: [email protected]
> Subject: FDC on Fire Pump
>
> Glad its Friday but I must be having a brain cramp..... Where does it 
> specify where the FDC ties into the pump discharge?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to